dhalleron
 - Louisville, KY
 - Master Electrician/Senior Fire Alarm Technician
Do I understand this right?
Can someone explain it better to me?
I'm sure I've been guilty if not derating many times in the past. I was just now trying to figure the right way to do it for a small resi job I have coming up.
I will be installing about 20' to 30' of 1" PVC from an outdoor panel to a junction box in the attic.
I will have the following circuits pulled in using conductors that should be dual rated THHN/THWN:
6 - 20 amp multiwire circuits - these are mostly small appliance circuits, dishwasher, disposal, bath GFCI etc.
1- grounding conductor
I assume my 6 multiwire circuits will be considered 9 current carrying conductors.
2008 Table 310.15(B)(2)(a) tells me I need to derate to 70%
Table 310.16 tells me #12 can handle 30 amps in the 90 degree C column.
This would allow me to use #12 wire on a 20 amp breaker I think because it would be derated down to 21 amps.
If I have to use the 75 degree column I believe I would need to go to #10 wire on a 20 amp breaker.
Thanks.