Does the grounding conductor for parking lot pole lights and ballfield pole lights have to be sized the same as the feeder conductors?
Does the grounding conductor for parking lot pole lights and ballfield pole lights have to be sized the same as the feeder conductors?
250.122 Size of Equipment Grounding Conductors.
(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.