Jorge medina
- Covina
I install a new panel out of one existing transformer 150 kva delta to star system , after I energize the panel , I found a problem one of the recept the hot side the isulation was rip and it was in contact with the metal box and send power back to the neutro bar of the pnl. I isolate the wire of the box and clear the problem.
Now this is my problem ; the breaker never trip,I check all the neutro system out of the transformer I check the ground system every looks fine the only ground I don't see is the one going from the transformer to the existing 400 amp pnl on the secondary side. They use the emt counduit like a ground from xfrm to the pnl