Calculate demand load for dryers in apt building
97catintenn
Columbia, TN
My exam question (based on 2005) was:
Calculate the demand load (in VA) of the dryers for and apartment building that has 12 units and 1 public unit (13 meters). The 12 units all have 5kw dryers and the public unit has 2 2kw dryers.
Answer: Table 220.54 Demand Factors for Household Electric Clothes Dryers
I have a total of 14 dryers so my demand factor is 47-(14-11) which equals 44%
(12 dryers X 5000w X 44%)+(2 dryers X 2000w X 44%) = 28160w
What do I do next to convert it to volt amps? 28160 wasn't one of the answers
Maybe? I can't remember for sure. I do remember the answers being in the neighborhood of
A. 24700
B. 47600
C. 65000
Not exact answers, but that was the basic spread. The question also gave information about all the appliances and such, but I thought it useless info and all I needed was the dryers for the calculation.
14 dryers
5 5 4
twice the no. between any 2 phases=10
12x5kw+2x4kw=64kw
demand factor t220.54 for 10 dryers, 50%
32000w
220.54 Electric Clothes Dryers ? Dwelling Unit(s). The
load for household electric clothes dryers in a dwelling
unit(s) shall be either 5000 watts (volt-amperes) or the
nameplate rating, whichever is larger, for each dryer
served. The use of the demand factors in Table 220.54 shall
be permitted. Where two or more single-phase dryers are
supplied by a 3-phase, 4-wire feeder or service, the total
load shall be calculated on the basis of twice the maximum
number connected between any two phases.
Kilovoltamperes
(kVA) shall be considered equivalent to kilowatts
(kW) for loads calculated in this section.
That must be it. To further confirm, the last sentence in the code you provided said that KVA shall be the same is KW in this example. And I do remember the answer being in VA.
Tough question. Thanks for the help :thumbsup:
I think you guys need to re-evaluate your answers.
-If I understand it correctly: 1. You have 12 household electric dryers located inside each unit?
2. Then you have two (2) common area dryers?
If I’m correct, then look at your answers again.
Each unit, which is an apartment, has one dryer rated at 5kw. And the public area has 2 dryers rated at 2kw each.
Sorry for not clarifying, I read your post and thought you just moved on :cool:
No, I’m here. I guess my question is for jumper.
I have a question for you. You had a multiple chose question with only three answers to choose from? Are you sure of those answers, because it would seem all three are wrong, including the 32Kw or Va.
No, I?m here. I guess my question is for jumper.
I am listening. I did not pick the answers, I merely tried to answer, your show.....
-The dryer demand factor= 46% [12 dryers-11=1] So: 47-1=46% DF allowed
-12 dryers (5Kw min)= 60KW
-60kw(.46)=27.6KW
Then onsite Laundromat:
-2 dryers (5Kw @ 100)=10Kw Note: No demand allowed
Ans=37.6kw or 37.6va
Heck, I could be wrong—seeing that I’m rusty :D
-60kw(.46)=27.6KW
Heck, I could be wrong?seeing that I?m rusty :D
