Please note the OP says "from the meter..."
This sounds like an installation where there will not be any outside disconnecting means - something that is very likely ammended by the local code.
In a similar manner, it's likely the fire code will want an outside disconnect.
The next step in this discussion will be 'what does the NEC mean by 'nearest' the point of service entry?'
I really don't have much concern over 6" of SER going through the wall to a main disconnect on the other side. I do have an issue with unprotected SER going up the wall, across the ceiling, and down the wall to a panel with six breakers in it.
If he's redoing the service, IMO, he needs to have a disconnect at the meter. Code finesse aside, it's simply stupid to not be able to turn things off without pulling the meter.
For the most part we install a main breaker panel in the basement around here with just a meter socket outside usually it is no more than 8' of unprotected cable going from the meter to the panel.
I agree that it would be better to use a meter main socket instead , but the cost of a main breaker meter socket is much more that just a meter socket.