What you have provided is just a small part of the entire spec. What I would be looking for is something more in the written part of the spec.
In my opinion it certainly appears to be ungrounded and that the NER is part of a ground detection system and not a grounding resistor as one would think. What I don?t see is that it is supposed to do should it detect ground current. What I would be looking for is an alarm of a breaker being tripped.
If I were to compare it to something it would be an ungrounded delta where a ground detector is used to illustrate some sort of concept. If one line goes to ground you want to know about it before a second line goes to ground.
In your case there's a bigger risk when one is isolating the system from ground because of human safely and electric shock because of the 150MA sensitivity.
Again, with out having access to the entire spec this is only an assumption.
Oh, and the 50hz, is this domestic or foreign?