NEC 240.21(B)(2) states that taps not over 25' long must terminate in a single circuit breaker, so a Main Lugs Only panel would not comply. However, 240.21(B)(1) makes no such stipulation for taps not over 10' long. As I read it, that means I can run a feeder tap to a MLO panel as long as the tap conductor is no more than 10' from the tap to the lugs. Is that correct?