gadfly56
Senior Member
- Location
- New Jersey
- Occupation
- Professional Engineer, Fire & Life Safety
We are replacing the controller and fire pump for a customer.  Because of the size of the new controller, we have to relocate it about 10' away from the previous location.  The AHJ wants us to use 2-hour rated conductors into the new controller.  All well and good (although not necessary; once you are in the fire pump room you don't need the 2-hour rated conductors).  We are on 2008 in NJ.  The building was constructed, as far as I know, around 1985.  I don't know which edition NJ was on then, but say the 1984 or '87.  Article 695 didn't appear until 1996.  Where would I find the information on the rating required for the conductors (if any) back then?  I ask because the conductors from the disconnect on the 10th floor to the fire pump on the 17th floor are THW and wouldn't meet today's 2-hour or the previous 1-hour rating requirement.  I want to know if I'm going to be the bearer of bad tidings to the customer.
	
		
			
		
		
	
				
			 
				
 
 
		