panelboard clearance

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What does the code say about how far a gutter may extend out in front of a panelboard. Example: an 18" gutter mounted below a 6" deep panel?

It is permitted as long as you can maintain the maximum distance of 6". That may require building out the disconnect off of the wall something like this:

Disconnect%2520over%2520Transformer.jpg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Are those listed fittings on the fmc for the bonding wires?

Nope, whoever installed those just used the screws on the fittings. :happysad:

Those jumpers aren't required since there was an EGC and bonding jumper within the raceway.
 