There is a 100A outdoor lighting panel which has a 100A main breaker and is located 40 feet from the switchboard who feeds it.  The designer put a 125A breaker feeding the lighting controller.  The designer specified a #1 AWG size cable.  The load on the lighting panel is 3.5KVA, and is not expected to increase at all.  The breakers are molded case.
When I asked why he did not put a 100A breaker instead of the 125A, he said that he did it from a coordination standpoint. He wanted the 100A breaker in the lighting panel to trip first before the breaker in the switchboard, that is why he upsized the breaker in the switchboard a bit larger.
I stated that there is really no chance for the breaker in the lighting panel to trip due to an overload (thermal) and if there is a short/fault (magmatic)there will probably be a race between the two breakers, and they most likely will trip at the same time, not guaranteeing that the breaker in the lighting panel will trip first.
Was wondering as to your feedback.
Thank you.
Thank you.