Bond transformer guard?
sii
Nebraska
I am in the process of installing a 75 kVA transformer in our plant. I will be installing a guard in front of the transformer constructed of 2" x 2" square stel tubing. I couldn't find anything in the NEC but does this guard need to be bonded to ground in any way?
I do not see anything bonding this guard will accomplish, I can't see it likely being energized (unless you dug into one of the conductors feeding the transformer)
I agree, don't bother bonding it.
Have you considered bonded it simply to the transformer enclosure which should be bonded with an EGC?
I agree with templdl. My inclination is to bond anywhere one can reach between conductive surfaces. So if it is less than 8 feet from the guard to the xfm, I'd bond the two. This is not a code issue, it is a safety design issue.
ice