Concentric Knockouts
Will Wire
California: NEC 2020
Electrical Contractor
I am running EMT from the main service panel to a sub-panel. I am entering the sub-panel through concentric knockouts. An equipment grounding conductor is also installed in the conduit for attachment to a ground bar in the sub-panel. Does the code always require a ground bushing installed when an enclosure is entered with a metal raceway through concentric knockouts? I am in California and we are using the 2008 NEC.
And voltage over 250 volts to ground such as circuits in a 277/480 volt system.
See 250.97 which will point you to 250.92(B) excluding 250.92(B)(1)
Another place which doesn't apply to your install is where a raceway enclose a grounding electrode conductor as in 250.64(E)
And in some hazardous locations in the 500 area of the NEC.
I think that about covers it
What's the voltage, also some KO's are listed for bonding over 250 volts.
Rob,
Are there panels or disconnects with the KOs so listed? As far as I know the only things with "listed" KOs are boxes.
There could be be but I don't know for certain. By looking at the tangential KO's on Square D equipment I might guess that they're listed when over 250 volts but I'm unsure.
Some of those concentric knockouts can be a pain in the tush. Beyond what the NEC/or UL requires I personally would consider good judgment as to whether addition attention should be considered from a professional?s point of view.