I'm inspecting a residential service-panel upgrade when I notice #8 awg THHN copper wires terminated on the load side of a 50 amp two-pole breaker. These 3-wire branch circuit conductors in a nonmetallic-sheathed cable supply an electric range.
The breaker is 60/75 degree rated and so I understand by 2008NEC110.14(C)(1)(a) that these conductors are safely protected. But do I need to expose the range plug and range cord to see if these are also sized for 50 amps for their protection?
Thanks
Thanks