Dental office has a 11.6amp single phase 208-230V motor. 208V. coming into it. Lasted about 5 years. On 8hrs. a day.
Abeint temp. in the room is 100 degrees plus. Manufact. says 208V. is on the low side, and should
be bumped up to 230V. So my questions are: 1. Can the breaker serve as a disconnect for the line
side of the tranny? 2. I also will need a disconnect for the load side of the tranny, before the motor?
3. Sizing the tranny. Is it as simple as anything bigger then 11.6amps? Or is there more to it?
Any other things you can point out would be very much appreciated. Thank you for your help.