meternerd
- Athol, ID
- retired water & electric utility electrician, meter/relay tech
One other comment...
I noticed in the OP that there is still a 5 jaw meter. To meter a grounded wye ststem, you have to use a form 16 meter, which is a 7 jaw meter. If the utility did really hook up the bank ungrounded wye, then there should be no ground connection to any of the three neutral bushings on the bank. A tank ground that is not bonded to the bushing is OK in most states. It is permissable to connect an ungrounded service [250.24 (E) and 250.20.(B) (1)] if , when grounded, the voltage to ground on any ungrounded phase would be more than 150V, but I doubt many utilities would. If there is a ground connection on the neutral, then all bets are off and they should have connected the bare neutral conductor at the transformer bank and made the customer install a fourth wire in the service riser. It should then be bonded in the service disconnect panel as stated in 250.24 Then they should send all of the linemen involved back to school. I'm betting they wired it 3 wire ungrounded wye. If that's the case, ground detectors are required per 250.21 (B)