eric9822
- Camarillo, CA
- Electrical and Instrumentation Tech
We have a high resistance ground system and it has always been our practice to oversize the fuses on small motors to account for the possibility of the additional 5 amps of current when a ground fault occurs. For example, a 3 phase 460V 1/2 HP motor should use a 2 amp time delay fuse per Table 430.52. With a high resistance ground system that fuse would open in the event of a ground fault negating the benefit of the high resistance ground system. I was reviewing an engineering package for a new installation today and several small motors had the fuses properly sized per table 430.52 but lower then we would specify due to the high resistance ground. I called it out but figured I better find the exception that allows it and I can't. Is there an exception or was this one of those "under engineering supervision" things at the beginning and we have just kept doing it?