Curious if drawing above came in visible to all. Service is on north side of strip mall. Their is 10 units approx. service as viewed in drawing is together with a added ct which was existing. Only thing down field is the Meter and sub panel. Just curious on the Meter being bonded to casing of meter pan. I am running ground right thru meter without termination direct to Loadcenter. I did not bond ground to meter pan. For it would not be isolated all the way back to service. Where does the ground and neutral being separated end must go to service. Correct ? Or is their another way Please view drawing, still not sure here.
Since the drawing is a PDF it is not viewable in the forum but is an attachment that can be opened separately.
The thing that is not clear in the drawing is the locations of equipment drawn, and what is being supplied, as well as any details of same or separate buildings or structures. This information can change a lot of things that may or may not be allowed.
I am seeing on the left a meter supplying a 200 amp panel with main - likely located near the meter, this would be one service. Then from same meter another supply to a 400 amp switch (with the old meter location used as a junction box), and likely some distance from the meter but do not know if it is even part of same building. This would be a second service. If both services are on same building or structure it is likely violation of either 230.2 or 230.72.
If it is separate buildings it may be just fine, and if so it is service equipment and equipment grounding conductors are not needed until past the service disconnecting means.