TVSS

Status
Not open for further replies.
No nice answer

No nice answer

If the manufacturer of the TVSS will not recommend a breeaker, I would not use that product.

The TVSS is not a load, except briefly during a surge.

You could opt to size the OCPD to the wire feeding the TVSS.

The problem comes in that the magnetic element in the OCPD needs to be set above the likely current when the TVSS is doing its job. I know of no easy way to determine that value.
 
Typically a 30A breaker is recommended.

You want the physical location of the breaker to be closest to the incoming lug or main breaker.

Keep the leads absolutely as SHORT as possible.

Personally, I prefer not to have the panel vendor NOT supply the TVSS as I have a personal perference for the quality and supplier of the TVSS. I have it mounted on the side of the pnlbd in line with the breaker feeding it.


RC
 