mkgrady
 - Massachusetts
This customer with a small office building is having problems with damaged electrical equipment. I'm told he has had to replace a couple of small motors and a fancy gas water heater in a short period of time. He asked me to see if I can find a problem with his system.
The service is 400 amps single phase, 120/240 with two 200 amp main panels. All connections in meter socket, MCBs and all circuit breakers seem good. At all points in the panels the voltage is 124/248. A little high but I'm thinking it is not damaging equipment. The power company has already been out to say the system on their end is OK.
My first thought is to install surge protection on both panels with the idea that it can't hurt and maybe it will help. Siemens makes a device that plugs in like a breaker. It takes the place of two CBs and it also contains two single pole breakers to reconnect the old circuits (there is no space in either panel). The cat # is QSA2020. There is also a unit that adds TVSS to the end of the catalog number. I'm wondering what the difference between the units is. In looking at the cut sheet the TVSS unit costs more and provides more insurance on connected equipment but I don't really care about that much. The cheaper unit is rated higher in Joules which seems better. What really has me stumped is the Intiial Clamping Level. The cheap one is rated 360 volts and the TVSS is rated 240 volts. I don't know what that means. Since the voltage is already over 240 how would that effect the one rated 240 volts?
Which unit would be better ? Any other ideas?