JDB3
- San Antonio, Texas
When figuring the 80% load of the wire for #12,  is it correct to use the 25 amp rating?
25 amps X 80% = 20 amps.:?
In wiring a wall heater 4,000 watts @ 240 volts (actual voltage at site is 245 volts), would # 12 NM (romex) be acceptable? No central heat, so they may run continuous.
wouldn't 4,000w/240v=16.67a? The 16.67=1.25%=20.83a which exceeds the rating of a #12 conductor it appears. As such is it #10 wire that should be used? #10 wire is rated 30a and you can use a 25at or 30at breaker to protect the wire.
Yes, but you should probably explain why and where you found it info as to the 125% for the OP.