tonype
- New Jersey
See 230.9 and 230.24.
90.2 Scope.
(B) Not Covered. This Code does not cover the following:
(5) Installations under the exclusive control of an electric
utility where such installations
a. Consist of service drops or service laterals, and associated
metering, or
I do not see where this install violates any clearance rules however I don't see any strapping or support.
From NESC 234C3(c): "Wires or cables attached to and run alongside the installation shall have clearances from the surface of the installation not less than 75mm (3 in.)"
FYI: 10 ft. over decks and balconies, 3 ft in any direction from windows, doors, porches, decks, fire escapes or similar locations with two exceptions, service drops above top level of a window, or windows not designed to open.
Are NESC codes available for free legal online viewing like NFPA?