lowvoltman
I'm looking to transform 480v single phase down to 440v(or close to it) with a load of 250 amps. 480 is too far off, it's got to be as close to 440 as I can get. Any suggestions? Does anyone make a buck-boost that size? Thanks!
I frequently see similar questions about buck-boost transformers posed here.I'm looking to transform 480v single phase down to 440v(or close to it) with a load of 250 amps. 480 is too far off, it's got to be as close to 440 as I can get. Any suggestions? Does anyone make a buck-boost that size? Thanks!
From the OP...You didn't say if it was 1ph or 3ph but assuming it's a 3ph wye .
May be cheaper to go with an actual step down transformer, may even be somewhat easier to get.
Wayne, why would the BB transformer need to be rated at 110KVA? You size the transformer base on the secondary voltage not the total voltage. 32 volt @ 250 amps is 8KVA.
I believe 110 kva would be appropriate for a standard step down transformer. A buck boost of the 15 kva variety should suffice for this application. I was trying to find an off the shelf one but 10 kva is the biggest I've found. Thanks
From the OP...
Actually, it's voltage difference.Wayne, why would the BB transformer need to be rated at 110KVA? You size the transformer base on the secondary voltage not the total voltage.
I think it would be best to order one from a custom transformer manufacturer which should be a 4-6 week item at most. Quite often you may find a standard design in the catalog but it may likely be a non stock item anyway.
After searching some, I find that bucking a 480 volt is only offered in a 24/48 volt secondaries, which will push the KVA to about 12, and will be special order![]()
as a custom transformer supplier, I can tell you all that a custom transformer most often costs LESS than the closest "standard" transformer and typically have lead times at least from us of 3 weeks, with 2 weeks not uncommon & 1 week most of the time when required.....