GerryB
Senior Member
- Location
- woodbridge, ct. USA
Recently I installed a 200 amp manual transfer switch for a customer. I mounted it adjacent to the panel, removed the SEU from the panel and fed the top line side of the transfer switch, re-fed the panel from the center load of the transfer switch. The local utility doesn't like it. They have one paragraph in their guide book about generators. "Such installations require an adequately sized double throw or open transition switch. The switch must be on the load side of the main disconnect switch and metering equipment. The switch must disconnect the Company's lines from the Customer's wiring before the generator can be connected to supply electricity. " The only way to do this with the 200 amp service is to change the meter outside to a combination meter with 200 amp breaker. I thought the transfer switch became the main disconnect and the existing panel becomes a sub-panel, and one local electrical inspector agreed. From the utility's standpoint nothing has changed. The SEU is still hot from the meter outside to the first point of disconnect, (3 or 4 feet). Any replies?