How would I calculate the size wire/pipe for a 200a feed about 150' from switchboard to 200A panel? Foreman said to run a 200a feed. Copper in EMT. THanks.
 
Count your conductor Number and size. Go to chapter 9 Tables 4 & 5 and calculate the needed pipe size. If it is 3 phase with a full neutral then you need 4- 3/0 copper usually thhn wire for 200 amps. If a ground is needed then #6 based on T.250.122
 
How would I calculate the size wire/pipe for a 200a feed about 150' from switchboard to 200A panel? Foreman said to run a 200a feed. Copper in EMT. THanks.


It would be good for you to know this, so do the home work for this project...........but I have to ask..........Is that not his (the formans) job?



Sorry, alittle ticked off here........some guy on a music forum bought a couple mics for 15000 dollars and is nervous about telling his wife. Turns out he's a doctor. geez.........


Thanks for letting me vent.

Back on topic....conductor size..any relative voltage drop.....whats the ambient temperature.... Don't forget to size to the 75 degree column.