mkgrady
Senior Member
- Location
- Massachusetts
The unit is a Sundance 880 Series, Optima. It requires a 60 amp circuit, 240 volts (not 120/240). It will be installed outside a single family home. The owner is going to make a concrete pad for it before it is delivered
6-2 NM from a 60 amp gfci in the main panel to a disconnect on the outside of the house. Disconnect will be >5 feet from tub and < 50 feet from tub and within sight
Bury PVC conduit from the disconnect to the tub with #6THHN, two hots and insulated ground to tub control box
Any metel within 5 feet of tub will be connected together and to the tub bonding lug
It is normal to have the conduit run right into the open space under the tub? Or is it normally run to the outside of the tub and flex into the open area. I'm having trouble picturing how to have the PVC come out of the ground and next to the tub and somehow getting it into the conduit entrance hole.
I don't know if the pad will be getting reinforcing rods. If it does I will bond them along with any other metal within 5 feet. I am confused about whether or not I also have to run a wire around the perimeter of the tub. If so would it be layed into the concret or just buried a few inches into the dirt around the perimeter of the pad?
Am I missing anything? All corrections and sugestions welcome. Thanks
6-2 NM from a 60 amp gfci in the main panel to a disconnect on the outside of the house. Disconnect will be >5 feet from tub and < 50 feet from tub and within sight
Bury PVC conduit from the disconnect to the tub with #6THHN, two hots and insulated ground to tub control box
Any metel within 5 feet of tub will be connected together and to the tub bonding lug
It is normal to have the conduit run right into the open space under the tub? Or is it normally run to the outside of the tub and flex into the open area. I'm having trouble picturing how to have the PVC come out of the ground and next to the tub and somehow getting it into the conduit entrance hole.
I don't know if the pad will be getting reinforcing rods. If it does I will bond them along with any other metal within 5 feet. I am confused about whether or not I also have to run a wire around the perimeter of the tub. If so would it be layed into the concret or just buried a few inches into the dirt around the perimeter of the pad?
Am I missing anything? All corrections and sugestions welcome. Thanks