jojo
Member
- Location
- Philippines
- Occupation
- Electrical Engineer
Hello guys. I just want to know if there's a standard method of sizing a generator:
a) For non-motor loads, is it okay if the generator size is calculated based on the demand load? My understanding is we size it based on the demand load times 1.25 (the 80% maximum loading of generator). Please advise.
b) For combination of motor and non-motor loads, do we size it like the way we sized for the main breakers? (max FLA motor *2.5) + FLA of the remaining motors plus non-motor loads? Or do we size the highest motor load on the starting kVA then the remaining motors using its FLA plus the demand load of the non-motor loads? Please help. Thank you.
a) For non-motor loads, is it okay if the generator size is calculated based on the demand load? My understanding is we size it based on the demand load times 1.25 (the 80% maximum loading of generator). Please advise.
b) For combination of motor and non-motor loads, do we size it like the way we sized for the main breakers? (max FLA motor *2.5) + FLA of the remaining motors plus non-motor loads? Or do we size the highest motor load on the starting kVA then the remaining motors using its FLA plus the demand load of the non-motor loads? Please help. Thank you.