Here is a little background on my situation before I ask the actual question. In a typical installation on my site we have conduit that extends from our panels or MCCs or MVC's up to a ladder type cable tray system. In a typical installation the feeder or branch circuits are pulled through the conduits up to the tray where they are then ran out to their respective loads or sources.
The question is this. I realize that the code requires for an electrical raceway or system to be electrically continous. I am also aware that both a conduit and a cable tray can be used as an equipment bonding conductor. With that said though, in this installation the equipment grounding conductor is actually pulled in with the circuits or feeders and in most cases is bonded to the conduit through a bond bushing inside the gear or MCC. When this is done I realize that the conduit is in effect bonded and is at the same potential as the equipment bonding conductor itself. The problem I am having however is that in alot of cases there is a gap between the conduit and the cable tray. The cable tray is bonded to the building steel itself and the conduit is usually bonded through the use of a bonding bushing or a locknut to the gear itself.
Since the code states that the ground shall be electrically continous it is my understanding that there should be a bond jumper between the conduit and the cable tray since there is an air gap. It is also my understanding when selecting the size of this bond jumper you should use table 250-122 so that way the bond jumper will be able to handle any fault current.
Am I correct in my interpretation?
The question is this. I realize that the code requires for an electrical raceway or system to be electrically continous. I am also aware that both a conduit and a cable tray can be used as an equipment bonding conductor. With that said though, in this installation the equipment grounding conductor is actually pulled in with the circuits or feeders and in most cases is bonded to the conduit through a bond bushing inside the gear or MCC. When this is done I realize that the conduit is in effect bonded and is at the same potential as the equipment bonding conductor itself. The problem I am having however is that in alot of cases there is a gap between the conduit and the cable tray. The cable tray is bonded to the building steel itself and the conduit is usually bonded through the use of a bonding bushing or a locknut to the gear itself.
Since the code states that the ground shall be electrically continous it is my understanding that there should be a bond jumper between the conduit and the cable tray since there is an air gap. It is also my understanding when selecting the size of this bond jumper you should use table 250-122 so that way the bond jumper will be able to handle any fault current.
Am I correct in my interpretation?