What are they talking about when they say...

A short-circuit protective device shall be provided on the load side of, or as an integral part of, the service disconnect, and shall protect all ungrounded conductors that it supplies.

I appreciate an clarification anyone can give me on this!! Thank you!!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Note that this is in a section of the Code for Over 600v
I'm not sure I understand your question but it basically states that a "Service Disconnect" will include or be adjacent to the short circuit protective device (fuses or otherwise).
This is similar to 230.91 for services under 600v.
 