I have a service with a tap ahead of the service disconnects to feed a fire pump service rated switch. What governs the length of the service tap conductor inside of a building?
The AHJ
I can't see where the fire pump service should be treated differently as far as 230.70(A)(1) is concerned.
That seems to be confirmed by 695.6, but with YOU asking the question I feel I'm overlooking something and am about to learn.![]()
Am I not correct that Art 240 is for feeder and transformer taps and not service taps ?
Possibly Art 695 is vague in order to be in line with Art 230![]()
Yes, that was my thought as well. I have a 4000 amp service and need to install a tap before the mains but the engineer is showing a tap length of about 35'. Also he's undecided on the raceway required for enclosing the tap conductors.
Here's a photo of part of the switchboard. The incoming utility will be in the crown box section at the top left and the fire pump switch will be at the extreme right with a few more sections in between. The tap will be in the top of the first section on the left. IMO the raceway feeding the switch will need to be in 2" of more of concrete.
![]()
Will the Fire Pump disconnect switch be part of the switch gear?
With that arrangement I would not doubt the AHJ accepting without the encasement especially if that's a dedicated switchgear room. I see similar accepted in these parts frequently.
side note: Is the duct not a violation ?
I can not see the issue here!!! Can some body explain to me it? The disconnect switch inside of the electric room will be as any other service switch taped from the load side of the CT's now ,from the disconnect switch inside of the electric room the ( 1200amp ) feeder wire need to meet the 2hrs fire rate or be in a system with two hrs fire rate, you have a few option to do this meeting the requirements for 695.6B. If the issue is the underground part or encase in concrete you have the option of use RHH wire rated 2hrs fire rate with regular EMT pipe (steel fittings) supported every 6 feet with the RHH wire inside.
So you're saying that 30'-35' tap run in conduit overhead to the 1200 amp switch is code compliant under the NEC or is it a NYC thing?
Actually you right 25 feet is the maximum tap length .Go over it will need underground or encase in a least 2 inch concrete .
Actually when you mention tap I assume that you consider the service wire as a tap conductor in that case the wire have to meet the tap rules. Personally I dont see it as a tap conductor based on 240.2 ,but in the same time overcurrent device (Service Switch) need to be installed near of the point of entry by section 230 of code, now I been involved in installation when the service feeder for the fire pump was probably 30 feet but , it is inside of the electric room and also due to large equipment installed there It have been not other way to intall it .Not an issue with the inspector.But we all knows that pass an inpection doesn't means that the intallation was correct. I used rigid metal conduit for that intallation. The only limit probably is the word near of the point of entry. Sorry if I'm wrong with the section mentioned before but I answer from my phone and no code book avalaible now.Curious, what Code Article do you use for the 25 ft limit ?