Table 250.66 Over 1100 cu./ Over 1750 Al.

Status
Not open for further replies.

wireguy8169

Senior Member
Location
Southern Maine
Ok,

Never really thought about it because I have never had to deal with it, but when sizing a grounding electrode conductor according to table 250.66 when you get to Over 1100kcmil cu. or over 1750kcmil Al. it seems by the way its written that 3/0 or 250kcmil is as large as you ever have to go, unlike the grounded conductor you would need to go to 12 1/2 % over 1100/1750kcmil.

Hope this make sense, but not sure if my thinking is correct, if not please refer me where to look.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, #3/0 cu maximum size for GEC, over 1100 kcmil 12.5% for the bonding jumper. Same would apply to a transformer. Here's a photo of the #3/0 GEC and a 350kcmil bonding jumper:

20080209_60.JPG
 

DARUSA

Senior Member
Location
New York City
Yes, #3/0 cu maximum size for GEC, over 1100 kcmil 12.5% for the bonding jumper. Same would apply to a transformer. Here's a photo of the #3/0 GEC and a 350kcmil bonding jumper:

20080209_60.JPG

Infinity What is the reason to have 4 cables on the ungrunded wire ( and) 12 wires on the neutral ( grounded) wire? Harmonic?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Infinity What is the reason to have 4 cables on the ungrounded wire ( and) 12 wires on the neutral ( grounded) wire? Harmonic?

Actually it's a 500 kva with 5 sets of 500 kcmil ungrounded and 10 sets on the neutral (200%) for a Broadway theater with a large dimming load feeding a 1600 amp switchboard.
 