Ok,
Never really thought about it because I have never had to deal with it, but when sizing a grounding electrode conductor according to table 250.66 when you get to Over 1100kcmil cu. or over 1750kcmil Al. it seems by the way its written that 3/0 or 250kcmil is as large as you ever have to go, unlike the grounded conductor you would need to go to 12 1/2 % over 1100/1750kcmil.
Hope this make sense, but not sure if my thinking is correct, if not please refer me where to look.
Thanks
Never really thought about it because I have never had to deal with it, but when sizing a grounding electrode conductor according to table 250.66 when you get to Over 1100kcmil cu. or over 1750kcmil Al. it seems by the way its written that 3/0 or 250kcmil is as large as you ever have to go, unlike the grounded conductor you would need to go to 12 1/2 % over 1100/1750kcmil.
Hope this make sense, but not sure if my thinking is correct, if not please refer me where to look.