Table 250.66 Over 1100 cu./ Over 1750 Al.

Status
Not open for further replies.

wireguy8169

Senior Member
Location
Southern Maine
Ok,

Never really thought about it because I have never had to deal with it, but when sizing a grounding electrode conductor according to table 250.66 when you get to Over 1100kcmil cu. or over 1750kcmil Al. it seems by the way its written that 3/0 or 250kcmil is as large as you ever have to go, unlike the grounded conductor you would need to go to 12 1/2 % over 1100/1750kcmil.

Hope this make sense, but not sure if my thinking is correct, if not please refer me where to look.

Thanks
 
Yes, #3/0 cu maximum size for GEC, over 1100 kcmil 12.5% for the bonding jumper. Same would apply to a transformer. Here's a photo of the #3/0 GEC and a 350kcmil bonding jumper:

20080209_60.JPG
 
Yes, #3/0 cu maximum size for GEC, over 1100 kcmil 12.5% for the bonding jumper. Same would apply to a transformer. Here's a photo of the #3/0 GEC and a 350kcmil bonding jumper:

20080209_60.JPG

Infinity What is the reason to have 4 cables on the ungrunded wire ( and) 12 wires on the neutral ( grounded) wire? Harmonic?
 
Infinity What is the reason to have 4 cables on the ungrounded wire ( and) 12 wires on the neutral ( grounded) wire? Harmonic?

Actually it's a 500 kva with 5 sets of 500 kcmil ungrounded and 10 sets on the neutral (200%) for a Broadway theater with a large dimming load feeding a 1600 amp switchboard.
 