jmellc
Senior Member
- Location
- Durham, NC
- Occupation
- Facility Maintenance Tech. Licensed Electrician
Looked at a bath fan unit the other day. Fan, light, night light & heater combo unit. 4 switch leg feeds to unit. Done with separate 14/2's; cable 1 has common neutral to all, & black to fan. 2 has hot to light, white to night light, 3 has black to heater, white capped off. All grounds connected. 2 of the cables have been overheating; jackets discolored & partially melted. Same with main feed to switch. I see why switch leg cables may overheat, with no hot/neutral balance in cable. But feeder to switch is hot/neutral/ground & should have even load. Fan has been locking up a long time. I guess extended lock up could cause overheating but also should trip the breaker, a 15 amp sp breaker. It is a GE breaker though, maybe that is the problem. I will do an amp check when I go back there.
When I replace the unit I will wire with flex and THHN conductors.