NM and Plastic Sprinkler Pipe
George Stolz
Windsor, CO NEC: 2023
Hospital Master Electrician
Has anyone ever been rejected for having Rolex in physical contact with plastic sprinkler piping? The sprinkler guy says he just failed for this, because "NM sheathing is petroleum based and will compromise the sprinkler pipe." I think the inspector is nuts - opinions?
I AGREE WITH THE CALL!!!!!!!
"The inspector is NUTS''
x
Once , I lost my Rolex in a 4" sprinkler pipe, and I was really upset, so I went and bought another one, only it cost twice as much as the first one I lost. :D
Sorry George, I just couldn't help myself.
The closest I've been to this is having a can light up against the orange plastic pipe they use. The installed said the plastic will melt. I told him to boil water in a paper cup over an open fire.
In your case, I would say the movement of the pipe and the can over time (caused by expantion and contraction, from heating and cooling) would rub a hole in the pipe. It may take 30 years but it can happen.
Check out page 6 and 53 of this PDF:
http://www.spears.com/flameguard/FG-3-1010_0911_web.pdf
This amazes me!
Don?ts
? Do not use edible oils such as Crisco as a gasket lubricant.
? Do not use petroleum or solvent-based sealants, lubricants, or fi re stop
materials.
? Do not install tape, insulated wire or cable in direct contact with CPVC.
? Do not use any glycol-based solutions as an anti-freeze.
? Do not mix glycerin and water solutions in contaminated containers.
? Do not use solvent cement that exceeds its shelf life or has become
discolored or jellied.
? Do not allow solvent cement to plug the sprinkler head orifi ce.
? Do not connect rigid metal couplers to CPVC grooved adapters.
? Do not thread, groove, or drill CPVC pipe.
? Do not use solvent cement near sources of heat, open fl ame, or when
smoking.
? Do not pressure test with air.
? Do not pressure test until recommended cure times are met.
? Do not use ratchet cutters below 50? F.
? Do not use CPVC pipe that has been stored outdoors, unprotected and
is faded in color.
? Do not allow threaded rod to come in contact with the pipe.
? Do not install Spears? FlameGuard? CPVC Fire Sprinkler Products in
cold weather without allowing for expansion.
I would like a little more toughness in my sprinkler pipe, what did they make it out if .... tissue paper ....... on no, NM does not degrade tissue paper.
Almost all sprinkler heads are thermal...about the only static that could cause one to open would be a lightning strike.