This is the first one I have had to quote and have a few questions.

I have the POCO bill for the month with the most usage with a total KW 26.44 with a 3phase 208v service

With the Generac brand would this require the 45 kw unit

Concerning the wiring I have an existing 200amp main lug panel protected with a 200amp breaker in the meter center, I would need to remove the feeder from the panel and route thru the transfer switch than back to panel and install a conduit with a,b,c neutral between transfer switch and generator plus control wiring in seperate conduit.
 

KWH

Senior Member
This a dentist office with 2 A/C's and a clothes dryer and air compressor/ air dryer.
 