My response is based on the inference that this is a circuit that does not have a neutral, and more to the point it is not a MWBC. I also infer that the load is 60 amps, as opposed to a 60 amp breaker serving a load that draws something less than 60 amps. You have it right. The voltage across the circuit is 208, not 240, and not a pair of 120's.
If this were a MWBC, and if it served two independent 120 volt loads, then the other person would be right.
MWBC is multiwire branch circuit, which what you have described seems to be if one wire is a system neutral.Thanks for your reply.
The breaker will feed a 60 amp 120/240 v 3 wire receptacle which will have a single phase temporary panel plugged into it.
What is 'MWBC'?
Hello
Question is - What is the correct va calculation for a 2 pole 60 amp cct. at 208 volts. I get 12,480 va. (208x60)
Peng says it's 14,400 va (2x120Vx60)
It is a 2 pole breaker in a 3 ph panel.
Thanks for any reply's
Sounds like the receptacle is going to supply a 120/208 1? 3W panel via a receptacle.Im trying to think why the P.Eng said 14,400?
For 2 Pole cct:
P=V(p-p)*I
= 208*60 = 12480
Unless this is for a residential panel in which case P=240*60, but you clearly state 208V,3Ph system so not residential panel?
Sounds like the receptacle is going to supply a 120/208 1? 3W panel via a receptacle.
Potential max connected load is 60A?120V?2Lines=14,400VA