We have a scenario here that we have an existing 200amp panel being feed with 4#3/0 THWN copper wire. We are upgrading the panel to a 400 amp panel, we are going to reuse the existing 200 amp feeders and simply add one additional 200 amp line to it, which will now become a paralleled 400 amp feeder to the new 400 amp panel.
The electrician ran the new line and pulled in 4#3/0 THHN-2 Copper wire.
My Question, Will THWN and THHN-2 comply with section 310-4 below?
PARALLEL FEEDERS SHALL COMPLY WITH NEC 310-4.
? BE THE SAME LENGTH
? HAVE THE SAME CONDUCTOR MATERIALS
? BE THE SAME SIZE IN CIRCULAR MILLS
? HAVE THE SAME INSULATION TYPE
? BE TERMINATED IN THE SAME MANNER
Thanks for your suggestions.