Wire bond still required

Status
Not open for further replies.

tommy

Senior Member
Location
Maryland
I have a two section panel with a parallel feed to the first section. Then a parallel feed to the second section. The panels have two 4" nipples to interconnect the two. Does the nipple do the bond or would a wire bond be needed? With two nipples would I need a bond to go thru both nipples since paralleled or one sized to the over current amperage? I am having a brain freeze on this for some reason. I want to say the nipples are the bond or one bond wire sized accordingly. What you say.
 

Smart $

Esteemed Member
Location
Ohio
Need more details to give a concise answer.

Service conductors/equipment or feeders/subpanel?

Voltage to ground over 250V?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the nipples are metallic and qualify as an EGC in 250.118 then no wire type EGC is required.
 