Hi all, I have an install for a split AC System in a home. The HVAC installer is trying to have me use a tray cable that is approved for direct burial and sunlight resistant. From what I can find in the code, I don't think this cable is approved for instalations in a home or conceled in walls. Am I mistaken? Can I staple it to the outside of the house? I see nothing that permits stapling but I also see nothing that prohibits it.
photo (5).jpg
 

jzadroga

Member
Location
MA
I'm in Massachusets and only an electrician can install the wiring. I believe he might be able to do the low voltage if he pulls an electrical permit but there is no low voltage in this case. I think he is trying to get me to buy it from him but thats not the question. I dont think I can use this wire in a home.
 

Smart $

Esteemed Member
Location
Ohio
... The HVAC installer is trying to have me use a tray cable that is approved for direct burial and sunlight resistant. From what I can find in the code, I don't think this cable is approved for instalations in a home or conceled in walls. Am I mistaken? ...
Tray Cable (Type TC) is not permitted to be installed outside of a raceway or cable tray system except in an industrial environment [336.12(2)]
 

jzadroga

Member
Location
MA
Thats what I thought but wanted to verify. Since the HVAC guy was trying to supply the wire I figured I'd better check it out. further searching on honey wells website shows this cable as a mini split cable but i cant see where it is worth using. If it has to be in a raceway than why not just use thwn. It would bee cheaper and easier I think. For my install 14/3 UF cable is cheaper and meets code.

Has anyone else heard about this cable?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Tray Cable (Type TC) is not permitted to be installed outside of a raceway or cable tray system except in an industrial environment [336.12(2)]

What would be a good reason for this when looking at the label on the cable?

THHN-OK
600 volt-OK
pvc jacket-OK
Tray Cable-Not OK
 

kwired

Electron manager
Location
NE Nebraska
Tray Cable (Type TC) is not permitted to be installed outside of a raceway or cable tray system except in an industrial environment [336.12(2)]

Yet it has a dircet burial rating on it, maybe for a direct buried cable tray? (I guess the industrial environment maybe could be direct buried - but am guessing in most cases they would use a raceway.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
There is no reason to run TC. You can run any wiring method you want. Many manufacturers supply a cord for the unit but I usually run power to the disconnect outside and then run nm inside the walls to a JB outside then flex to the unit with Thwn or use UF all the way. You can use the TC cable in a raceway.
 

Smart $

Esteemed Member
Location
Ohio
Yet it has a dircet burial rating on it, maybe for a direct buried cable tray? (I guess the industrial environment maybe could be direct buried - but am guessing in most cases they would use a raceway.
I was just citing one "required" wiring method using TC. TC is not permitted to be direct buried unless it is marked [suitable for] direct burial. But the OP mentioned something about stapling to wall, which certainly isn't direct burial...!!!
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
From what the local HVAC folks tell me that's a "standard" cable the manufacturer supplies...
and I imagine in many areas it is installed without raceway, but as pointed out, doing so would be a Code violation.
My memory tells me all 4 condcutors are current carrying so I'm not sure you4 14/3 wg
UF would be a good substitute.
Locally most use the TC and install it in a raceway.

Another long fought argument here is the need for a disconnect at the inside fan motor.
 

donselectric

Senior Member
Location
nh
i did one of those in mass and when i got there the ac guy had run the cord and left it
hanging out the wall tywrapped to the freon lines. i can tell you it was a pita to hookup
as the manufacturer only provides 2 1/2 ko's and there were two of those cables and my feed.
i went upstairs to see how he connected it...wish i didnt he had cut off on of the grounds out of
one cable guess he figured he had one in the other.....its a listed package so i wasnt arguing with
the cord issue and it passed insp....:
 