Back-fed c/b
I understand the 120% busbar rating rule.
Example: 200A service panel with a 150A main c/b.
200A X 1.20 =240A -150A = 90A.
Do I use a 45A back-fed c/b? Because 45A+45A =90A.
No, IMO that would mean a 90 amp dp breaker.
Is this the article you are using.
705.12(D)2) Bus or Conductor Rating. The sum of the ampere ratings of overcurrent devices in circuits supplying power to a busbar or conductor shall not exceed 120 percent of the rating of the busbar or conductor.
The size breaker you use depends on the size of the solar system. The 120% rule defines the maximum you can use. The maximum is definitely a 90A breaker in your case.
In a 204/120 panel, there are two busbars. Each busbar is rated for 200A in your case. Both the main and the solar breaker are double-pole breakers. Therefore each busbar can take one pole at 150A plus one pole at (up to) 90A.
Thanks, I understand now. I was reading another post with these figures, and I believe, they were talking about using a double-pole 45A c/b. I know it depends on your system size. I just want to clarify that 45A double pole c/b = 45A and not 90A.