Any experience with using the heavy duty Siemens PV disconnects?
Usually Heavy Duty, 600 VDC rated , Square D disconnects (model # HU361RB for example) are used as DC disconnects in PV arrays.
The problem? Each pole on the Square D 30A disconnect can only handle 11.5 A Isc @ 156% = 18Amp MAX - if all three poles are used.
According to my interpretation of their 2007 Data Bulletin, higher amps (up to the rating of the disco (30, 60, 100 etc AMPS)) may be disconected as long as they are routed through two poles to safely extinguish the 600 VDC arc.