No equipment ground on water heater

Status
Not open for further replies.

TimWA

Member
Rewiring a rental dwelling on low customer budget, do I have to pull a new circuit on an existing two-wire-only 220V water heater, or is it grandfathered in? Can I bond the WH case to adjacent copper plumbing bonded at the service? Fault current on plumbing would be momentary would it not?
 
Last edited:

stevebea

Senior Member
Location
Southeastern PA
Rewiring a rental dwelling on low customer budget, do I have to pull a new circuit on an existing two-wire-only 220V water heater, or is it grandfathered in? Can I bond the WH case to adjacent copper plumbing bonded at the service? Fault current on plumbing would be momentary would it not?

Momentary yes, compliant no.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I don't see a way this can be compliant without an EGC.

It may have been compliant at one time, but it does not comply with current rules.

IMO, if you mess with this circuit in any significant way you have to make it compliant.
 

TimWA

Member
See 300.3(B) ('05 is what I have here)

Momentary fault current is a "maybe". An element could fail in such a manner as to allow current to flow on the EG for an extended time.


Which is actually the case in any grounding or bonding scenario.
 