I need to model a 4160-480/277V, 1500/2000kVA transformer (Class AA/FA) which has 6.63% impedance.
Does anyone know if the proper calculation of short-circuit current at the secondary of the transformer is supposed to be based on the self-cooled rating (1500kVA, 1804FLA) or is it supposed to be based on the forced air rating (2000kVA, 2406FLA)?
Using an infinite bus at the primary the difference in calculated fault current is considerable (27210A self-cooled kVA basis, and 36290A forced air basis).