domelectric
- Sarasota, Florida
Hi guys. It is my understanding that all kitchen receptacles must be on a 20A circuit however, does a receptacle on a wall at 16 in AFF have to be on the SA circuit? Does this low receptacle have to be GFI protected? It is not serving counter top, within 6 foot of a sink, or in any other place that requires GFI protection except that it is in the kitchen. Thanks. BTW I've spent 30 minutes searching this forum for an answer before posting.
And thank you Charles E. Beck for your definition of an outlet in a past post: But in the language of the profession, in the language of the NEC, an outlet is essentially (but not quite exactly) the 2x4 or 4x4 box into which you install some electrical device. More exactly, an outlet is the tip of the wires that enter the box from within the walls, and that attach to an electrical device. I've been saying this for years.