When sizing a service when you combine continuous and non-continuous loads and come up with 170amps , you can breaker this at 200amps or is there a derating on the breaker also.
You really don't have to figure the continious loads in for the service, that's for the branch circuit.
What about 230.42?
Perhaps I shouldn't have said just branch circuits, but I was referring to calculating the load for services in 220. No where in the standard or optional method do I see where you count continuous loads, just largest motor.
Article 220 provides the requirements for calculating loads for Branch-Circuits, Feeders, and Services. There is nothing in the standard or optional methods for feeders and services about continuous and noncontinuous loads. Nor is there anything in Part II "Branch-Circuit Load Calculations" about continuous and noncontinuous loads.
You will have to look in Art 210, Art 215 and Art 230 for Branch-Circuits, Feeders and Services respectively, to find out how to apply continuous and noncontinuous loads when sizing conductors and OCP.