Article 220 provides the requirements for calculating loads for Branch-Circuits, Feeders, and Services. There is nothing in the standard or optional methods for feeders and services about continuous and noncontinuous loads. Nor is there anything in Part II "Branch-Circuit Load Calculations" about continuous and noncontinuous loads.
You will have to look in Art 210, Art 215 and Art 230 for Branch-Circuits, Feeders and Services respectively, to find out how to apply continuous and noncontinuous loads when sizing conductors and OCP.