dana1028
Senior Member
- Location
- San Francisco Bay area
I am resurrecting an old forum discussion [2007] in which Don made some comments about the needed bonding of the GEC when routed through other enclosures.
I have a photo from the 2011 "Electrical Grounding & Bonding" by Simmons.

Based on Don's reply to Pierre [see below], I gather the bonding within the enclosure is not necessary since all the conduits are already electrical connected [assumption - the top raceway is electrical/mechanically connected to the service cabinet].
Don's comments [2007]
Pierre,
Quote: Does it matter where the bonding occurs in the enclosure, such as at the point of entry or at a bus located inches away?
As long as the enclosure is metallic, the point of bonding between the GEC and the enclosure does not matter. If the GEC terminates on a bus, the bus would have to be bonded to the enclosure by a conductor with a an area equal to or greater than the area of the GEC. Bonding at both ends is only required when the enclosure is not electrically continuous. If you have a metal enclosure with a GEC passing through and the GEC is protected by a ferrous raceway, you could use standard locknuts on both of the raceways and a single bond to the enclosure and be in compliance with the rule in 250.64(E).
Quote: When thinking of this question, if bonding location is not important, then why are we required to bond at both ends of the enclosure?
The bonding requirement for a ferrous raceway is to make it electrically continuous. In the case of a raceway originating at a metallic enclosure, the GEC is bonded to the enclosure and to the other end of the raceway. There no code section that specifies the type of bonding that is required at the raceway to enclosure termination point. The section only refers to the Chapter 3 requirements, so standard locknuts would be permitted. If you are installing the GEC through a hole in the enclosure and the GEC is bonded to the enclosure, there is no additional bonding required.
Don
My question: I just want to make sure I am correctly understanding Don's previous comments. They sound logical, and I don't want to be making electrician's perform additional bonding if it is not required. Thanx for any feedback.
I have a photo from the 2011 "Electrical Grounding & Bonding" by Simmons.

Based on Don's reply to Pierre [see below], I gather the bonding within the enclosure is not necessary since all the conduits are already electrical connected [assumption - the top raceway is electrical/mechanically connected to the service cabinet].
Don's comments [2007]
Pierre,
Quote: Does it matter where the bonding occurs in the enclosure, such as at the point of entry or at a bus located inches away?
As long as the enclosure is metallic, the point of bonding between the GEC and the enclosure does not matter. If the GEC terminates on a bus, the bus would have to be bonded to the enclosure by a conductor with a an area equal to or greater than the area of the GEC. Bonding at both ends is only required when the enclosure is not electrically continuous. If you have a metal enclosure with a GEC passing through and the GEC is protected by a ferrous raceway, you could use standard locknuts on both of the raceways and a single bond to the enclosure and be in compliance with the rule in 250.64(E).
Quote: When thinking of this question, if bonding location is not important, then why are we required to bond at both ends of the enclosure?
The bonding requirement for a ferrous raceway is to make it electrically continuous. In the case of a raceway originating at a metallic enclosure, the GEC is bonded to the enclosure and to the other end of the raceway. There no code section that specifies the type of bonding that is required at the raceway to enclosure termination point. The section only refers to the Chapter 3 requirements, so standard locknuts would be permitted. If you are installing the GEC through a hole in the enclosure and the GEC is bonded to the enclosure, there is no additional bonding required.
Don
My question: I just want to make sure I am correctly understanding Don's previous comments. They sound logical, and I don't want to be making electrician's perform additional bonding if it is not required. Thanx for any feedback.
Last edited: