Distribution Panelboards with Fuses
faresos
Can we use copper bars in lieu of fuses for a distribution panelboard (or switchboard) as a disconnecting mean for the main switch? This board is fed upstream from 800A/3P fuses. We just need a disconnecting mean for this board since the source is located remotely in different room. Thanks in advance
I would normally recommend using an actual 'dummy-fuse', but above 800A I think you need to use a home built one.
jim
what's the lowest interrupting capacity that could be used with a dummy-fuse? ;)
mike
That would be zero amps.
AIC has to do with interrupting a fault, a dummy fuse would be expected to withstand a fault.
It is likely that it could have a relatively high SCCR, as the bus used is not likely to 'flex and deform' in such a short distance as a fuse.
Jim
I knew I couldn't fool You!
Mike
Am I missing something? Was the original question about disconnects (as opposed to fuses)? The panelboard has a disconnect and fused protection somewhere (in another room)? So no other disconnect is required (i.e. in sight of the panelboard). Correct?