A system was designed with 1500W heaters (each fused 10a) , and the AC in is 120VAc on a 15A circuit, 14awg.
They had intermittent tripping of the internal 15A breaker. More information came to light. With the box, temperatures reach to 51deg C (has a small internal boiler.)
My first thought was the breaker is too small. De-rating the breaker at about 55C, brings it to about 12A, which is 120X12A=1440W. If it was ambient temperature, this would still be marginal.
I suggested a 20A breaker on 12awg. De-rated brings it to 16A, which is 120x15A = 1920W.
The question came back, can we use the 20A breaker with the 14awg, if the conductor is only about 30" long.
They ran a short circuit test on 20A/14awg, and it didn't blow the internal breaker, but did blow the breaker for the receptacle they were using.
The end of the (short) wire welded to the screw.
Tell me what happened here?