The service to this room is 208Y/120V 60amp. Each filter assembly consists of 2 filters. We need to filter phase A, B, C & neutral. Therefore, 2 filter assemblies with 2 filters in each assembly. Each phase and/or neutral will penetrate the steel shield individually. The total shielded room is not UL listed. I guess if you looked at the total shielded room including the filters as a single  piece of equipment, the NEC would not apply. The filter assembly is a UL listed piece of equipment.