When suppling information for electrical service size when using VFD's, do you use the max drive rating or FLA from the motors. There is a debate in our office on what to use.
Yes, notice it says the DRIVE'S rated power, not the motor. That's because of two things:Like texie says 430.122 is where you want to look. I vaguely remember some debates going on but the section seems pretty clear to me. Feeders are sized at 125% of the drives rated input power.
Yes, notice it says the DRIVE'S rated power, not the motor. That's because of two things:So to avoid having to engineer each installation, the NEC just made it easy by saying 125% of the max Amp rating of the VFD, then there is no question of whether or not it is adequate. Overkill? Maybe a little, but better safe than sorry.
- VFDs, like NEMA starters, only come in certain sizes. People often put in VFDs larger than the load it is attached to, then later because the VFD is rated for a higher current, they CHANGE the motor to one that takes advantage of that, leaving the circuit incapable of handling the new current if it was sized for the original motor FLA.
- As mentioned, the VFD has losses and harmonic heating effects that do not factor into the circuit size if only looking at the motor FLA. The total amount of current represented in those losses and effects can themselves be affected by the design and appurtenances of the VFD, such as filters, reactors etc.
The rule in 430.122 only applies to the size of the conductor that feeds the VFD. It does not have anything to do with load calculations.
Item 1: I disagree, just because you have a size 1 starter but the motor only needs a size 0, you size the wire to the motor, not the size 1 starter. Of course, not so for the VFD.
Item 2: I'll stipulate to that. It just seems like there must be a better way to account for this instead of a blanket 125% adder to better accomodate situations like I mentioned in my previous post.
I didn't mean to imply that you need to size a circuit for maximum with a NEMA size starter, it was only an example of devices that only come in certain sizes. The difference with starters and drives is that because drives represent a singificant investment, people were tending not to swap them out, but rather to use what they have. For every 250HP drive on a 50HP motor, there are likely 100 250HP drives on 150-200HP motors. I'm doing a project right now with 7 150HP pumps, the Consulting Engineer has specified that the drives be rated 300A minimum, that's essentially a 250HP drive the way they are sized with most mfrs. I'm not to question the reasoning, I'm just putting in the drives. But I know, some day, some plant foreman will look at upgrading that system and in his budget assessment, he is going to take advantage of the fact that those drives are over sized. If the line conductors were sized for 150HP motors, he might be tempted to look the other way. That sort of stuff happens all the time and especially on retrofits where there is no inspection. That's the scenario that 430.122 is trying to address in my opinion.Item 1: I disagree, just because you have a size 1 starter but the motor only needs a size 0, you size the wire to the motor, not the size 1 starter. Of course, not so for the VFD.
Item 2: I'll stipulate to that. It just seems like there must be a better way to account for this instead of a blanket 125% adder to better accomodate situations like I mentioned in my previous post.
It is not referenced in Article 220 and there is nothing in 430 that tells us to us use that value for load calcualtions.Well, if that is true, you could end up with smaller service conductors than feeders in some situations.
See 430.122. This has been debated here before and I don't think there is consensus on this. For example, there was a recent post here about something like 20 each 3 HP motors with 5 HP drives and how to size the feeder. You can see that in a case like this 430.122 is a problem. I've said before that this is something I don't understand the reasoning on behind 430.122. Is this where we get to use sound engineering judgment?
Well, if that is true, you could end up with smaller service conductors than feeders in some situations.
Are you a sound engineer?![]()
I didn't mean to imply that you need to size a circuit for maximum with a NEMA size starter, it was only an example of devices that only come in certain sizes. The difference with starters and drives is that because drives represent a singificant investment, people were tending not to swap them out, but rather to use what they have. For every 250HP drive on a 50HP motor, there are likely 100 250HP drives on 150-200HP motors. I'm doing a project right now with 7 150HP pumps, the Consulting Engineer has specified that the drives be rated 300A minimum, that's essentially a 250HP drive the way they are sized with most mfrs. I'm not to question the reasoning, I'm just putting in the drives. But I know, some day, some plant foreman will look at upgrading that system and in his budget assessment, he is going to take advantage of the fact that those drives are over sized. If the line conductors were sized for 150HP motors, he might be tempted to look the other way. That sort of stuff happens all the time and especially on retrofits where there is no inspection. That's the scenario that 430.122 is trying to address in my opinion.
Is it a perfect solution? No, but like many of the code provisions it is a compromise to try to have people err on the side of safety.
that is actually pretty common.
I didn't mean to imply that you need to size a circuit for maximum with a NEMA size starter, it was only an example of devices that only come in certain sizes. The difference with starters and drives is that because drives represent a singificant investment, people were tending not to swap them out, but rather to use what they have. For every 250HP drive on a 50HP motor, there are likely 100 250HP drives on 150-200HP motors. I'm doing a project right now with 7 150HP pumps, the Consulting Engineer has specified that the drives be rated 300A minimum, that's essentially a 250HP drive the way they are sized with most mfrs. I'm not to question the reasoning, I'm just putting in the drives. But I know, some day, some plant foreman will look at upgrading that system and in his budget assessment, he is going to take advantage of the fact that those drives are over sized. If the line conductors were sized for 150HP motors, he might be tempted to look the other way. That sort of stuff happens all the time and especially on retrofits where there is no inspection. That's the scenario that 430.122 is trying to address in my opinion.
Is it a perfect solution? No, but like many of the code provisions it is a compromise to try to have people err on the side of safety.